1 hour ago, immamac said:

Your drain line is clogged and your drain pan is full. 

This. 

 

1 hour ago, tchookem said:


Water dripping from under the AC unit. It pooled up on the foundation under the unit and has spread under the carpet and flooring in the hallway.
 
No water under the actual unit.
 
Any ideas?







https://cloud.tapatalk.com/s/66b92d0b25768/20240811_162005.mp4

If you have a small air compressor try getting a rag, creating a seal with the air nozzle and blowing down your overflow drain line. 

 

In the future try pouring down 1 cup white vinegar mixed with 1 cup hot water down the drain line you're about to blow out at least once a month. 

  • Like 2
Posted

Did it stop dripping?  Do you have a two story house?  I learned something at our last house.  The AC drain line ties into the drain system for the rest of the house, usually at upstairs sinks.  If you look at the plumbing under those sinks you might see a Y fitting with a hose attached to it.  This is where the AC drain line ties in.  Several times I found that sediment would clog that Y fitting and even if I blew out an obstruction it would still fill up because the clogs were still there at those Y fittings.  So I removed the pipe clamps and took a screwdriver and reamed out the fitting to clear it.  Voila.

Posted

(depending on the age of the AC install)

You will have a secondary / overflow drain line in your soffit & it is typically set over a window (kitchen) or near a door.  The idea is so you will see it & recognize the primary is clogged.

Additionally, building code since ______ (I don't know when) has required a "Float Switch" for the condensation pan, so either your system's installation date predates the code, your installer didn't put one in or you do have one & it's defective.

307.2.3.1: “On downflow units and all other coils that do not have a secondary drain or provisions to install a secondary or auxiliary drain pan, a water-level monitoring device shall be installed inside the primary drain pan. This device shall shut off the equipment served if the primary drain becomes restricted. Devices installed in the drain line shall not be permitted.

307.2.5: “Condensate drain lines shall be configured to allow the clearing of blockages and performance of maintenance without having to cut the line.”

image.png.2e8c34a847720cf7e37a4cdba13025c4.png

Posted
If you have a small air compressor try getting a rag, creating a seal with the air nozzle and blowing down your overflow drain line. 
 
In the future try pouring down 1 cup white vinegar mixed with 1 cup hot water down the drain line you're about to blow out at least once a month. 
Bleach works too
Posted
7 minutes ago, Mother mopar said:
On 8/11/2024 at 6:16 PM, BurntOrange&White said:
If you have a small air compressor try getting a rag, creating a seal with the air nozzle and blowing down your overflow drain line. 
 
In the future try pouring down 1 cup white vinegar mixed with 1 cup hot water down the drain line you're about to blow out at least once a month. 

Bleach works too

Bleach is too abrasive on PVC IMO.

  • Hook 'Em 1
  • Like 1
Posted (edited)
21 hours ago, Ojo Rojo said:

Did it stop dripping?  Do you have a two story house?  I learned something at our last house.  The AC drain line ties into the drain system for the rest of the house, usually at upstairs sinks.  If you look at the plumbing under those sinks you might see a Y fitting with a hose attached to it.  This is where the AC drain line ties in.  Several times I found that sediment would clog that Y fitting and even if I blew out an obstruction it would still fill up because the clogs were still there at those Y fittings.  So I removed the pipe clamps and took a screwdriver and reamed out the fitting to clear it.  Voila.

Spot on where the problem may lie for many. Another great option to clear the pipe is using a shop vac. Make a good seal with the shop vac to that pipe going up to the AC unit. Some nasty crap will get pulled into the shop vac. shop vacs run $75-100 at Home Depot. Good to have a shop vac on hand with water problems.

Before reconnecting, see if water is correctly flowing down from the open pipe, near the drip pan. I think it’s good for the average homeowner to go through this issue once so they’re aware of the low maintenance to prevent it.

 

Edited by Nice Guy Eddie
Posted
2 minutes ago, Mother mopar said:
36 minutes ago, BurntOrange&White said:
Bleach is too abrasive on PVC IMO.

If that was the case, then we never use bleach in the washing machine.

You aren't putting 50/50 bleach in your washing machine.....it's far more diluted. 

Posted
On 8/12/2024 at 11:11 AM, Ojo Rojo said:

Did it stop dripping?  Do you have a two story house?  I learned something at our last house.  The AC drain line ties into the drain system for the rest of the house, usually at upstairs sinks.  If you look at the plumbing under those sinks you might see a Y fitting with a hose attached to it.  This is where the AC drain line ties in.  Several times I found that sediment would clog that Y fitting and even if I blew out an obstruction it would still fill up because the clogs were still there at those Y fittings.  So I removed the pipe clamps and took a screwdriver and reamed out the fitting to clear it.  Voila.

FYI, trying to clear a blockage at the lowest point of a pipe can lead to a big mess. You may have a gallon of stagnant water and algae built up behind the blockage. Make sure you a bucket when the blockage clears. Nasty stuff.

Posted
17 hours ago, Nice Guy Eddie said:

FYI, trying to clear a blockage at the lowest point of a pipe can lead to a big mess. You may have a gallon of stagnant water and algae built up behind the blockage. Make sure you a bucket when the blockage clears. Nasty stuff.

Yes, for sure.

Posted
On 8/13/2024 at 8:10 AM, Mother mopar said:
On 8/11/2024 at 6:16 PM, BurntOrange&White said:
If you have a small air compressor try getting a rag, creating a seal with the air nozzle and blowing down your overflow drain line. 
 
In the future try pouring down 1 cup white vinegar mixed with 1 cup hot water down the drain line you're about to blow out at least once a month. 

Bleach works too

*MAYBE* a cap-ful of bleach to 1 gallon of water.  Better to stick with vinegar & not damage the pipes.

Posted
Our techs advise vinegar instead of bleach.
I am on the Milwaukee battery system & got this ½ priced on a closeout. Works great on the shitter, the sink & there's no need to drag an air hose up into the attic.0dec71e99d1cabafe3ab4615d23328dd.jpg
  • Like 1
Posted
I am on the Milwaukee battery system & got this ½ priced on a closeout. Works great on the shitter, the sink & there's no need to drag an air hose up into the attic.0dec71e99d1cabafe3ab4615d23328dd.jpg

You need more fiber in your diet.
  • Like 1
Posted

You need more fiber in your diet.


No, I need my kids to not use ⅛ of a roll every time they drop a deuce & the wife & daughter to not clog the bathroom sinks with their hair.

Posted
On 8/11/2024 at 6:16 PM, BurntOrange&White said:

This. 

 

If you have a small air compressor try getting a rag, creating a seal with the air nozzle and blowing down your overflow drain line. 

 

In the future try pouring down 1 cup white vinegar mixed with 1 cup hot water down the drain line you're about to blow out at least once a month. 

Create a seal with a shopvac on the line outside works, too.

Posted
4 hours ago, ROFL BOX said:


No, I need my kids to not use ⅛ of a roll every time they drop a deuce

"Would you like to hear about our lord and savior, Bidet?"

  • Haha 1
Posted
On 8/11/2024 at 6:36 PM, tchookem said:

Thanks. I blew some air down the drain line, and this came out. I'm guessing it was the clog.20240811_165841.jpg

Something, something...South Austin's mom.

Posted

I’m hearing more than a few people in Houston running into this problem the past few weeks. I have to wonder if the power outages could have increased the problem with ACs not creating condensation plus hot houses equaling increased algae growth in the condensation pipes.

  • Hook 'Em 2
Posted
2 hours ago, CooterBrown said:

I've been pouring bleach down the drain pipe for 20+ years.  I like to live dangerously.

I am *absolutely not* an AC professional, merely repeating what I have been told over the decades about the bleach thing. 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.



×
×
  • Create New...